Guest TiffanyAr Posted April 8, 2015 Report Share Posted April 8, 2015 I have recently been advised that I do not require fire detection in an area that operates at +3C as the likelihood of a fire starting is low. However there are a lot of electrical apparatus in the area and the area is only manned during night operation so is left unmanned during the day. I feel that this area should have fire detection - please could you provide some guidance for fire detection at low temperature. Kind regards Quote Link to comment Share on other sites More sharing options...
Tom Sutton Posted April 9, 2015 Report Share Posted April 9, 2015 A fire alarm should be installed and a aspirating systems should be used, if standard detectors are unsuitable. (i.e. because of low temperatures) Check out this european guidance http://www.insuranceeurope.eu/uploads/Modules/Publications/1202469724_article231.pdf Quote Link to comment Share on other sites More sharing options...